SS fastners for Hot dip Galvanised steel = Problem??

Status
Not open for further replies.

jherbert

Mechanical
Aug 3, 2002
79
Hi,

If s/s fastners (bolts, nuts and washers) are used with Hot Dip Galavanised Steel - any corrosion problems anticipated?

In hostile damp environment, what would be the excepted life span? any ideas? Cheers,
 
Replies continue below

Recommended for you

The stainless steel parts are in direct contact with zinc-coated carbon steel? The parts will be exposed to a hostile, damp environment? You can anticipate galvanic corrosion among your components, and the expected lifetime would be short.
 
The change in lifetime versus using galvanized fasteners to galvanized sheet will be fairly modest because typically with fasteners the area of the fastener is small compared to the area of the object it fastens to. Secondly, the stainless fastener will be passive and very little corrosion current can be generated by it. The surrounding zinc surface coating is already sacrificial to its iron substrate, so I predict very little life shortening of the system.
 
Perhaps I should clarify my original post. The stainless steel/zinc couple would corrode and may render the threaded joint unserviceable.
 
I agree with this insight of CoryPad. All the harm done by the galvanic couple will be concentrated at the contact between the stainless and the zinc. If this point is structurally critical, it's a inadvisable materials combination and galvanized fasteners should be used.
 
Thanks for your comments,

Are they Any other solutions?

Presently, galv fastners are corroding very quickly, in under 3-5 years become unservicable.

If S/S is little better, any other choice? am hoping for 10 years lifespan ??

Cheers,
 
Stainless fasteners for use on Galv. connections are O.K., as long as the total fastener is SS & not a SS bolt w/ a Galv. Nut. Any joint corrosion will be the Galv. parts, not the SS items. Of particular note are Cooling tower bases & structures that are continually damp. These will hold up maybe 10 to 15 years w/o corrosion, if the galv. application is not disturbed, IE: field welding and then zinc coating. Hope this helps.
 
The other thing that you see done is to use non-metalic or coated washers. This greatly reduces the galvanic issues. Stay with SS bolt and nuts, but isolate them from direct contact with the Zn.

= = = = = = = = = = = = = = = = = = = =
Corrosion, every where, all the time.
Manage it or it will manage you.
 