I've read about the incident, the public description and photos are eerily familiar. Our company, an electric utility, lost a 280 megawatt unit in the mid-1990s. The circumstances have a lot of parallels. Coincidence... maybe, maybe not.
The unit we lost was coal fired, same as St. Clair Station. The fire had nothing to do with the boiler or coal combustion.
Due to operator error, an off-line unit's generator was accidentally connected directly to the electrical grid. This caused the generator to respond as an electric motor and rapidly accelerate (along with it's steam turbine) toward synchronous speed (3600 rpm). (Perhaps the "letting go" you heard about.)
During the acceleration, mechanical damage occurred, throwing the turbine / generator out of balance. Vibration cause several big problems:
Ruptured a hydrogen cooling line which then exploded as a result of gross sparking in the generator. (An explosion was reported at St. Claire).
Vibration ruptured turbine lubricating oil lines, which ignited as a result of the hydrogen explosion. (Notice the black smoke coming from St. Claire).
Vibration pulled the machine's anchor bolts (about 4" diameter x 4' long) out of the reinforced concrete turbine / generator pedestal.
The combination of electrical shorts, hydrogen explosion, lube oil fire, and structural damage put the unit out of operation for well over a year. I handled the civil-structural rebuild along with reinstallation of the factory overhauled several hundred ton generator stator.