We are looking at a couple different options for installing an SRW/MSE wall. This wall was originally designed as an SRW type wall. It is near the bottom of steep slope and in front of a river. Thus there are relatively long grid lengths. It varies in height up to maybe 14' tall and the slope is about a 1V:1.5H or 1V:2H. They did some soil 'probing' and found:
“Approximately 1-foot of low bearing capacity soils overly what appears to be a combination of very dense slope wash soils over a layer of limestone over shale. The slope wash contains many large limestone slabs and from visual observation of the limestone in the slope it appears to be approximately 6-12 inches in thickness and is underlain by shale. Based on the DCP values it is doubtful that helical coils would be able to penetrate to sufficient depths for adequate resistance”
To reduce the excavation into this shale/rock, we are looking into designing the wall using the Stable Face MSE wall method as outlined in the FHWA-NHI-10-024 and FHWA-CFL/TD-06-001. Or possibly anchoring some steel pipe (running parallel to the wall) into the shale/rock with rock bolts (?). Then lapping the grid around the pipe and back to the wall.
I have a few questions and was hoping for some feed back:
1. While the Geotech will most likely give us their insight, I am wondering what the stability of limestone over shale is like? And/or can shale be "rock bolted" to?
2. Any other ideas for this situation?
3. I see Hilti has a product line for "rock bolts" however it is not found in the US. I'm having a hard time find any other similar products, any suggestions? Basically there would be a good number of these so the capacity does not need to be extremely high. Also I'm trying to keep the complexity to a minimum although I'm sure testing will be required. Some sort of threaded rod / epoxy anchor?
EIT
“Approximately 1-foot of low bearing capacity soils overly what appears to be a combination of very dense slope wash soils over a layer of limestone over shale. The slope wash contains many large limestone slabs and from visual observation of the limestone in the slope it appears to be approximately 6-12 inches in thickness and is underlain by shale. Based on the DCP values it is doubtful that helical coils would be able to penetrate to sufficient depths for adequate resistance”
To reduce the excavation into this shale/rock, we are looking into designing the wall using the Stable Face MSE wall method as outlined in the FHWA-NHI-10-024 and FHWA-CFL/TD-06-001. Or possibly anchoring some steel pipe (running parallel to the wall) into the shale/rock with rock bolts (?). Then lapping the grid around the pipe and back to the wall.
I have a few questions and was hoping for some feed back:
1. While the Geotech will most likely give us their insight, I am wondering what the stability of limestone over shale is like? And/or can shale be "rock bolted" to?
2. Any other ideas for this situation?
3. I see Hilti has a product line for "rock bolts" however it is not found in the US. I'm having a hard time find any other similar products, any suggestions? Basically there would be a good number of these so the capacity does not need to be extremely high. Also I'm trying to keep the complexity to a minimum although I'm sure testing will be required. Some sort of threaded rod / epoxy anchor?
EIT