Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Stagger distance for rebar lap splices

Status
Not open for further replies.

Engingguy

Civil/Environmental
Jun 9, 2016
19
0
0
US
I am looking in ACI 318-14 for a spec for the stagger distance between lap splices but can't find one. I am using #4 epoxy coated rebar, 60,000 psi. Concrete is 3000 psi and the splices are Class B. I need to come up with a better splice detail note than "Just stagger the splices so the concrete won't develop a crack in the weakened plane".
Thanks in advance.
 
Replies continue below

Recommended for you

Thanks, that was useful.
I have a triangular slab with upper and lower mats, and placing the splices while trying to maximize the use of 20 ft lengths is quite interesting. Moving a splice to provide clearance from another places it closer to yet another splice. Got er done, though.
 
Status
Not open for further replies.
Back
Top