Standard Voltages in Panama

Status
Not open for further replies.

mbk2k3

Electrical
Nov 18, 2010
97
I'd like to know what the standard voltages are in Panama with respect to industrial plant design.

medium voltage distribution = 13.8kV?
medium voltage distribution = 4.16kV?
low voltage 3 phase = 240V?
low voltage 1 phase = 120V?
 
Replies continue below

Recommended for you

inbk2k3,
My former employer about 20+ years ago was asked to bid for steel on the Panama Canal revamp. In the bid would be service centers at each end by the locks. I had found out which voltages were standard and 60Hz for the whole country. Bid was to high I guess.
3ph 480/277 volts wye
3ph 240 volts delta ungrounded
3ph 240 volts delta grounded "B" ph.
3ph 240/120 volts delta center tap
3ph 208/120 volts wye
1ph 120/240 volts
3ph 4160/2400 volts wye
3ph 2400 volts delta

One end of the canal was 13.8/7.97kV wye.
Other end was 13.2kV delta.
In other words, just like USA, including the NEC
Hope this helps,
Dave
 