Hello
I have a building with a class III standpipe system that is also fully covered with an autotmic sprinkler system (combined system). I'm hydraulically calculating the system and the HMD floor has 5 standpipes. How many of those am I supposed to supply?
The Code says:
5-9.1.2* Hydraulic Calculation Procedure.
Hydraulic calculations and pipe sizes for each standpipe shall be based on providing 250 gpm (946 L/min) at the two hydraulically most remote hose connections on the standpipe and at the topmost outlet of each of the other standpipes at the minimum residual pressure required by Section 5-7. Common supply piping shall be calculated and sized to provide the required flow rate for all standpipes connected to such supply piping, with the total not to exceed 1250 gpm (4731 L/min).
I would greatly appreciate it if someone helped interpret this clause, especially "and at the topmost outlet of each of the other standpipes".
Thanks
I have a building with a class III standpipe system that is also fully covered with an autotmic sprinkler system (combined system). I'm hydraulically calculating the system and the HMD floor has 5 standpipes. How many of those am I supposed to supply?
The Code says:
5-9.1.2* Hydraulic Calculation Procedure.
Hydraulic calculations and pipe sizes for each standpipe shall be based on providing 250 gpm (946 L/min) at the two hydraulically most remote hose connections on the standpipe and at the topmost outlet of each of the other standpipes at the minimum residual pressure required by Section 5-7. Common supply piping shall be calculated and sized to provide the required flow rate for all standpipes connected to such supply piping, with the total not to exceed 1250 gpm (4731 L/min).
I would greatly appreciate it if someone helped interpret this clause, especially "and at the topmost outlet of each of the other standpipes".
Thanks