SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
I've got a four story building motel that requires a standpipe (the top floor is 34' above lowest level of fire department access) but I don't want to use a fire pump.
5-7* Minimum Pressure for System Design and Sizing of Pipe.
Standpipe systems shall be designed so that the system demand can be supplied by both the attached water supply, where required, and fire department connections. The authority having jurisdiction shall be consulted regarding the water supply available from a fire department pumper.
Standpipe systems shall be one of the following:
(1) Hydraulically designed to provide the required waterflow rate at a minimum residual pressure of 100 psi (6.9 bar) at the outlet of the hydraulically most remote 21/2-in. (63.5-mm) hose connection and 65 psi (4.5 bar) at the outlet of the hydraulically most remote 11/2-in. (38.1-mm) hose station.
Exception No. 1: Where the authority having jurisdiction permits pressures lower than 100 psi (6.9 bar) for 21/2-in. (63.5-mm) hose connections, based on suppression tactics, the pressure shall be permitted to be reduced to not less than 65 psi (4.5 bar).
Exception No. 2: In other than high-rise buildings, the authority having jurisdiction shall be allowed to reduce the minimum pressure requirements of this section if the building is protected throughout by an approved automatic sprinkler system.
For exception #2 who would be the authoriity having jurisdiction? Is it the building code or local fireman?
5-7* Minimum Pressure for System Design and Sizing of Pipe.
Standpipe systems shall be designed so that the system demand can be supplied by both the attached water supply, where required, and fire department connections. The authority having jurisdiction shall be consulted regarding the water supply available from a fire department pumper.
Standpipe systems shall be one of the following:
(1) Hydraulically designed to provide the required waterflow rate at a minimum residual pressure of 100 psi (6.9 bar) at the outlet of the hydraulically most remote 21/2-in. (63.5-mm) hose connection and 65 psi (4.5 bar) at the outlet of the hydraulically most remote 11/2-in. (38.1-mm) hose station.
Exception No. 1: Where the authority having jurisdiction permits pressures lower than 100 psi (6.9 bar) for 21/2-in. (63.5-mm) hose connections, based on suppression tactics, the pressure shall be permitted to be reduced to not less than 65 psi (4.5 bar).
Exception No. 2: In other than high-rise buildings, the authority having jurisdiction shall be allowed to reduce the minimum pressure requirements of this section if the building is protected throughout by an approved automatic sprinkler system.
For exception #2 who would be the authoriity having jurisdiction? Is it the building code or local fireman?