Star Delta Motor - AC Induction 3ph 1

Status
Not open for further replies.

wingnut2551

Electrical
Nov 17, 2006
3
Now that I know that I have a Star Delta Motor, can this motor be connected on the Line Run wiring using a standard motor starter or do I still need the Star Delta Starter?
 
Replies continue below

Recommended for you

The answer depends on the motor HP or kW and the available short circuit at the starter (what kind of voltage drop will you get).

______________________________________________________________________________
This is normally the space where people post something insightful.
 
Yes, you can always choose to connect a Y-Delta motor in Delta only. All the other issues are related to consequences, and with a 10HP motor there are not likely to be any.

JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> faq731-376
 
The choice to use a star delta starter is often load related. If the motor is still driving the original load it may have some problems starting in delta. If you have only the motor and are driving an easy starting load you are probably OK.