How can I wire a star-delta motor ( six lead) to a VFD ? The motor has leads ( U1, V1, W1 , U2, V2 and W2. thanks
 
Replies continue below

Recommended for you

Wire it for the voltage corresponding to your grid voltage. That is the voltage (or, rather V/Hz) that your VFD will deliver. Not mentioning some special possibilities that exist.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
There are a lot of inter-dependent parameters. What are the motor nameplate voltages in star and delta, and what is the VFD output voltage? Also what is the VFD maximum output frequency and what is the motor nominal frequency (or rated speed)?


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Unless you have something special, six-lead motors (suitable for star-delta starter) are designed to run in delta. Star connection is only used during starting on a star-delta starter.

If so, you want to wire it in delta for VFD application.

Rafiq Bulsara
 
I'll politely disagree with Rafiq, at least for motors in the IEC world. Below 7.5kW motors are typically 230V delta / 400V star. Above 7.5kW motors are typically 400V delta / 690V star.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
ScottyUK:

No offence taken. All information is useful.

I would think dual voltage rating would be posted on the name plate. Perhaps that is what the OP meant by star-delta motor, then what you said is absolutely correct.

If the name plate indicates single voltage and the motor has six leads, it is usually meant for delta. At least that what I had come across in six years of experience in the IEC/India in the 80's. I thought by star-delta motor the OP meant a motor used on a star-delta starter, which probably was not correct.

Thanks



Rafiq Bulsara
 
Shall we sum it up in one sentence?:
Wire it for the voltage corresponding to your grid voltage.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
IEC, Star:delta is normally used for a 1.73:1 voltage adjustment.
NEMA Star:delta is normally used for starting, star to start, delta to run.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Well said, Muthu. Gunnar has also summed it up concisely.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
If you are going to remove three of the cables (leaving three), then make sure you have the correct cross-section for the load/distance required.
 