Hello GusD,
Great post!
My only concern is the information contained in your Step 1, as the actual motor FLC rating will vary between manufacturers.
For example recently we were asked to provide a quotation on a start package at 355kW, 415VAC 3-phase. Similar tables to that described in your Step 1 suggested and FLC of 560 amps, however when we reviewed actual data for motors available throughout Australia found that this could be anywhere between 530 amps and 630 amps. In addition if you analyse data for submesible motors, you will find that the FLC is almost always somewhere between 10% and 25% higher than that of a standard cage motor.
Due to the above-mentioned experiences and many other similar ones, where possible I like to refer to the motor 'nameplate' FLC rating and service factor, for the selection of switchgear, cables etc, and for setting up of the overload relay.
Regards,
GGOSS