Start Stop for booster Pumps

Status
Not open for further replies.

mengbly

Mechanical
Mar 17, 2013
8
Hello everbody

can anyone please help me in answering the below questions

1. what is the logic behind number of start/stops for domestic water pumps, is there any formula or calculations for the same ?

2. How to calculate the expansion tank size for the booster pumps, is the tanks size also related to the number of starts and stops of the pump??

thanks
 
Replies continue below

Recommended for you

Booster pumps can either be constant speed (older design type) or variable speed.

With a constant speed, the expansion tank is a must. With variable speed, it is a good idea to buffer the start up and shut down of the pumps.

With a variable speed pump, the on/off cycle is not as critical since it is not a full start, but I would assume 5-10 minutes between starts.

For sizing the tank, the manufacturers typically have a sizing page on their website. I use amtrol and look at the well pump expansion tank section.
 
To expand a little bit, electric motors don't like stop/start cycles, which reduce their life because of the extra heat resulting from the starting current. Somewhere deep in the fine print, motor manufacturers publish a limit in starts per hour above which they would prefer to not honor a warranty. Motors that are sold into price sensitive markets (like hydronics) are built with relatively little safety factor for anything, including stop/start cycles.



Mike Halloran
Pembroke Pines, FL, USA
 