Hi guys,
I reviewed yesterday a problem in an isolated diesel motor-synchronous generator group ("island" system).
The generator supplies to a compressor and a battery charger.
Basic motor diesel data:
- 800rpm nominal.
- uses a hyrdotransmission to regulate the power to the generator.
- limit speed to disconnect generator: 500rpm.
Generator data:
- Brushless synchronous 400Vrms, 70kVA, 3000rpms nominal, surge current > x2 In,
transient voltage deviation: +/-15% (5% in 500ms) at 100% load on/off
freq.:50Hz, dynamic transients +/-10%
They have problems when the compressor starts from the AC supplied by the generator.
The transient is quite out of specifications (see adjoint). Voltage lowers to 260Vrms!, 141A.
Additionally to this fact, the current drawn by the battery charger have a very strong 5th harmonic.
Questions are:
- In the initial transient, frequency doesn´t seem to chage so much, but voltage so. why?
I forgot quite a lot of sync generators in "island" connection, could appear here the "out of sync" torque angle problem and trip the protections? It seems that the generator keeps supplying the peak start current for quite longer time than usually expected (700ms).
- the battery charger draws a quite high 5th harmonic, could cause any side effects in the generator control or working?
- Sensible solution possibilities (for the start transient) could be use:
1) softstarter, 2) star-delta start 3) ¿bypassable per phase inductor could work?
Regards
I reviewed yesterday a problem in an isolated diesel motor-synchronous generator group ("island" system).
The generator supplies to a compressor and a battery charger.
Basic motor diesel data:
- 800rpm nominal.
- uses a hyrdotransmission to regulate the power to the generator.
- limit speed to disconnect generator: 500rpm.
Generator data:
- Brushless synchronous 400Vrms, 70kVA, 3000rpms nominal, surge current > x2 In,
transient voltage deviation: +/-15% (5% in 500ms) at 100% load on/off
freq.:50Hz, dynamic transients +/-10%
They have problems when the compressor starts from the AC supplied by the generator.
The transient is quite out of specifications (see adjoint). Voltage lowers to 260Vrms!, 141A.
Additionally to this fact, the current drawn by the battery charger have a very strong 5th harmonic.
Questions are:
- In the initial transient, frequency doesn´t seem to chage so much, but voltage so. why?
I forgot quite a lot of sync generators in "island" connection, could appear here the "out of sync" torque angle problem and trip the protections? It seems that the generator keeps supplying the peak start current for quite longer time than usually expected (700ms).
- the battery charger draws a quite high 5th harmonic, could cause any side effects in the generator control or working?
- Sensible solution possibilities (for the start transient) could be use:
1) softstarter, 2) star-delta start 3) ¿bypassable per phase inductor could work?
Regards