gaux
Mechanical
- Jan 27, 2009
- 48
hi, thanks for your always good ideas, now i just thinking on a new project on my table, that´s a motor that moves a propeller, that start on pitch 0, and i have calculated the mechanical losses.. and they are 116 kw´on 1600 rpm, the idea is to run the motor without load till 1600 with VFD (with VFD rated to 150 or 180 kw), (motor is 700 kw and four poles) and then, disconnect VFD and after a litle delay, something like 0,5 s, connect on direct connection the power supply to the motor, 400 V, but my question is What do you think about idea? i think the current will be really low, and is it possible to calculate the time for accelerating..... if we have a load if we have a load that starts with 0 and changes with the formula
181+ (0,0002*n^2) where n is speed rpm
thanks for your time.....
181+ (0,0002*n^2) where n is speed rpm
thanks for your time.....