magneticted
Electrical
- Mar 5, 2004
- 51
Hi guys, thanks for your response to my lasst thread regarding "starting current". After further discussions with the utility company, they are now going to use a korndorffer auto transformer with 85% tap.The motor will be rated at 650 kw (6pole) 11kv / 50 hz, and has a starting current value of 252A ( 6 x 42A ). The ulitily company is stating that the starting current must not be greater than 190A. I calculate at 85% tap the starting current will be 182A ( 0.85 x 0.85 x 252 ). Three questions, firstly is this calculation correct, 182A is the value seen at the 11 kv busbar. Secondly, is thier a motor + transformer magnetising current which can influence the calculation and make the 182A value higher. And thirdly as this is a korndoffer type I assume their will be no transient currents occuring at switch over. At the moment we have enough accelerating torque to start the pump on open valve at 85% tap.