I have to calculate the voltage drop in case of DOL starting a 6.6 kV induction motor (squirrel cage).
I used starting PF=0.3.
My boss said that PF=0.3 is too low for a MV motor.
I recall a calculation example from an IEEE book, that use for a LV motor, the starting PF=0.2. Therefore, I believe that PF=0.3 is quite generous, since there is no big constructive difference between a MV & a LV induction motor.
Obvious, using a low starting PF, will result an unacceptable voltage drop and consequently I have to consider an alternative starting method, such as: Y-D, autotransformer, series resistors or a capacitor bank.

Can anyone please advice me where I can find (a standard, paper or book) an advice on MV-HV induction motor’s, starting PF?

Thank you for your time.

 
Replies continue below

Recommended for you

I would contact a motor manufacturer. I typically use 0.2 for starting analysis.

I don't see why MV motors would behave much differently at locked rotor than LV motors, in terms of power factor.
 
It doesn't matter if it is MV or LV, the math is the same. But dpc is right, you are best to start with a motor manufacturer. MV motors are built to order: you can ask for pretty much anything you need but there are design limits and tradeoffs. I have worked on several MV motor projects doing TMS analysis where the motors were not yet selected, and every time a vendor came to us with a different motor, the numbers were always different and no two of the studies came out the same. I saw MV motors with as little as .15 and as high as .25 power factor at startup, but for a blind study I also always use a .20 pf.

Good paper on the subject from one of our members, Marke:

Word to the wise however: stay away from Y-Delta starting on MV motors. Transition spikes can damage other nearby electrical equipment and/or the torque spike can snap shafts on power train components. Primary resistors are nasty as well (think of the heat). Stick to Autotransformer, reactor or solid state starting.
 