Starting of concrete mixer.

Status
Not open for further replies.

SauravWest

Electrical
Dec 4, 2019
35
Dear sirs,

Could you please help me with electrical starting of concrete mixer for site? I think it has to be delta first and star later. How to understand the following picture?

Regards,
 
Replies continue below

Recommended for you

I'm assuming you are talking about a reduced voltage starter for an electric motor that runs a concrete mixer. the reason for reduced voltage start is to limit the starting current.

Wye-delta starters start the motor in wye configuration to apply 57% voltage across each winding. At the appropriate time, the motor starter reconnects the motor windings in delta to supply 100% voltage to each winding.
 