So you have about 2MW of 'running' motor and a 3MW source. Ouch. That is a tight squeeze. I see your concern and it's valid.
The cheapest solution is probably a pony motor. A 50HP motor that just gets the whole mess spinning. This requires a load type that can be spun up. Some sort of process that once the machine is running can be loaded by opening a valve, closing a valve, turning on a feed conveyor, etc.
What kind of load are you running with these motors?
Can you state an order that they will always start in? Can the two 1000's be started before the other 500?
Will the 1000s always be running together? There are some games you could play. Like getting one 1kHP started then use it to provide stored energy for starting the second unit since now you are closer to the 3MW limit. Don't know it depends on your processes.
Next cheapest is a Soft Starter. That can limit you to something like 200% rather than the aforementioned 8-900% hit.
Lets take a gander at the current. If we have the 500 and one 1k running, we have 1500hp x 746W/HP = 1.2MW
This translates to 1.2MW/4160 = 288A
The transformer is good for 3MW. 3MW/4160V = 720A
Now a 1kHP motor alone = 1000HP x 746W/HP = 0.746MW
Current 0.746MW /4160V = 180A
Now if that motor is direct-on-line(DOL) 180A x 8 = 1440A
So the already running 288A plus the DOL 1440A = 1728A. More than twice the transformer's ability. (I can't see! I can't see! Turn on the lights.)
But if you can limit that second 1kHP to 200%(depends on load type) then we have; 288A + (180A x 2) = 648A
720A - 648A = still a positive number.
If you can tell us about your loads others here can estimate your likelihood of a 200% start working for you.
Then you have your third option: VFD. Which realistically will probably provide a 125% start but will cost you a bundle. Now if your process would like a variable 1kHP then it could provide you with some nice flexibility.
Keith Cress
Flamin Systems, Inc.-