Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Stator cooling water conductivity?

Status
Not open for further replies.

frankiee

Marine/Ocean
Jun 28, 2005
138
0
0
CA
For Demin water stator cooling system
Why is the conductivity lower coming back from the generator then going to the generator.
Going to gen after HX and IX is about 0.13 micro Siemen/cm
Coming back from gen is about 0.5 micro Siemen/cm

Temp coming back is about 60 degree C
Temp going to gen is about 47 degree C

 
Replies continue below

Recommended for you

Status
Not open for further replies.
Back
Top