I ran across electricpete's post regarding how to measure stator/rotor air gap.
He specifically references API 1068. Reviewing API, I could not find that standard - but like how it's requiring physical confirmation of the air gap measurements.
Then he referenced API 541-1995, Section 2.4.7.16.
Is the information on how to do static measure the gap located in API 541?
Have a 3500 HP GE motor for a vertical pump being witness tested in Brazil and they’re saying they can’t measure air gap and are suggesting using the method outlined in API 541-2014, Section 4.4.7.2.4 – see attached. I don’t see how this method truly measures air gap. Has anyone seen the calculated air gap method be used in the past?
We have had problems with a couple of past motors where the air gap was eccentric - that motor stator/rotor rubbed against each other and we've had to get it rebuilt after 5 years service - and sustaining damage to the stator windings/ribs. Thus we now require review of air gap prior to leaving the motor factory.
He specifically references API 1068. Reviewing API, I could not find that standard - but like how it's requiring physical confirmation of the air gap measurements.
Then he referenced API 541-1995, Section 2.4.7.16.
Is the information on how to do static measure the gap located in API 541?
Have a 3500 HP GE motor for a vertical pump being witness tested in Brazil and they’re saying they can’t measure air gap and are suggesting using the method outlined in API 541-2014, Section 4.4.7.2.4 – see attached. I don’t see how this method truly measures air gap. Has anyone seen the calculated air gap method be used in the past?
We have had problems with a couple of past motors where the air gap was eccentric - that motor stator/rotor rubbed against each other and we've had to get it rebuilt after 5 years service - and sustaining damage to the stator windings/ribs. Thus we now require review of air gap prior to leaving the motor factory.