bacon4life
Electrical
- Feb 4, 2004
- 1,519
In thread608-259312 it was mentioned that the NESC requires wires to stay within the the Right of Way under blowout conditions. What section is that specified in?
In sections 230-234 I see only references to the clearances between wires and various objects, but no mention of property rights. I have come across 4 different situations, but haven't found a code reason to justify any of them. Does anyone apply something besides option 2?
1. Keep the wires on your ROW under nominal conditions.
2. Keep the wires on your ROW under blowout conditions.
3. Keep the wires on your ROW under all conditions.
4. Keep the wires on your ROW under all conditions, with enough clearance that some could put a building on the property line and still meet rule 234 clearances.
In options 1 to 3, it seems like you are interfering with the adjacent property owners right to fully utilize their land.
In sections 230-234 I see only references to the clearances between wires and various objects, but no mention of property rights. I have come across 4 different situations, but haven't found a code reason to justify any of them. Does anyone apply something besides option 2?
1. Keep the wires on your ROW under nominal conditions.
2. Keep the wires on your ROW under blowout conditions.
3. Keep the wires on your ROW under all conditions.
4. Keep the wires on your ROW under all conditions, with enough clearance that some could put a building on the property line and still meet rule 234 clearances.
In options 1 to 3, it seems like you are interfering with the adjacent property owners right to fully utilize their land.