Steam byproduct condensation 1
MNALE276
Chemical
Dear All,
How much chiller tonnage would be required to condense 135C steam at atmospheric pressure to water at 80C? 900 kgs of water is collected per hour.
MK
Sounds like homework to me. Homework is not allowed. Are you a student?
Good Luck,
Latexman
No sir, not homework, but I wish I was still doing homework! This is an actual design question for a line expansion at one of our manufacturing sites. We are entering phase II design and this detail was overlooked in the first phase. I may need to budget for an additional chiller to the 200 ton unit on-site.
MK
Chiller? what about a cooling tower? Do you know how to read a steam table to answer your own question?
Break the problem in two parts.
Go to your steam/water tables and look up the amount of heat that you will need to remove to cool/condense/sub-cool the water.
Then look for a cooling medium.
Do you have any sub-80C cooling water on site? If so then you are left just sizing a heat exchanger.
If you need to provide the cooling then why not look at a small cooling tower to do the job.
I don't see any need for a chiller unless you are going below ambient temp.
P.E. Metallurgy
Are you a degreed Engineer? This will help us help you.
Good Luck,
Latexman
Steam Tables
@ 133.5oC Hsteam = 2724.7 kJ/kg
@ 135.8oC Hsteam = 2727.6 kJ/kg
Therefore @ 135oC Hsteam = 2726.6 kJ/kg
@ 78.7oC Hwater = 329.6 kJ/kg
@ 81.3oC Hwater = 340.6 kJ/kg
Therefore @ 80oC Hwater = 335.1 kJ/kg
900 kg/hr x (2726.6 - 335.1 kJ/kg) = 2152350 kJ/hr = 2040034 Btu/hr = 170 tons of refrigeration
But as others have said, you don't need chilled water to condense 135oC steam to 80oC water. Cooling tower water (~ 35oC) is fine.
Good Luck,
Latexman
Yes, but many years removed from an engineering role. I apologize I realize I left a critical piece of information out of the problem statement. The steam byproduct has a contaminant that cannot be discharged to the atmosphere. The wastewater is collected and sent for treatment off-site. Thus the reason for not pursuing a tower. 170 tons was the estimate I initially had but thouoght this seemed awfully high.
I appreciate the help Latexman and all!
MK
Keep your process side in s closed system, but cool it with water that is looped through a cooling tower.
Or use a closed fan cooled unit for cooling, either like a fin-fan cooler or one from Graham Manufacturing (closed but with fans and water on the outside).
P.E. Metallurgy
135C steam at atmospheric pressure? Need some details. It may, already, be condensate with flash steam. In any case, cooling towers are cheaper option by CapEx and OpEx