Steam heating efficiency 1

Status
Not open for further replies.

bagdad

Industrial
Jan 20, 2005
1
What temperature should condensate leave a steam heating
coil (building air supply) to extract the best efficiency,
irrespective of discharge air temperature?
 
Replies continue below

Recommended for you

Maximum temperature should be the saturation temperature of water at the given pressure. If you are not recovering condensate then you can go for subcooling upto 50C by using thermostatic traps.