remp
Mechanical
- Sep 15, 2003
- 224
I have a new air handling unit, steam humidifer just commissioned and up and running. The primary side of the humidifier is hot water at about 140degC. There is a problem with the sparge pipes (pipes with holes that deliver the steam into the AHU). They are spitting out condensate as well as steam.
The sparge pipes are sloped back towards the humidifier which is about 3m below the AHU. The slope is not the problem. There is no consensate drain in the installation. It was not reckomended. There is a pressure equelizing line between the humidifier vessel and the AHU chamber. The manufacturer says the condensate should drain back into the humidifier via the supply/sparge pipes and the pressure equelizing line between the AHU humidifier chamber and the humidifier vessel should be sufficient to allow this. The equelising line is about 1/2 coper pipe.
It looks like the steam head is driving the condensate out and not allowing it to travel back to the humidifier.
Any suggestions what I should do??
The sparge pipes are sloped back towards the humidifier which is about 3m below the AHU. The slope is not the problem. There is no consensate drain in the installation. It was not reckomended. There is a pressure equelizing line between the humidifier vessel and the AHU chamber. The manufacturer says the condensate should drain back into the humidifier via the supply/sparge pipes and the pressure equelizing line between the AHU humidifier chamber and the humidifier vessel should be sufficient to allow this. The equelising line is about 1/2 coper pipe.
It looks like the steam head is driving the condensate out and not allowing it to travel back to the humidifier.
Any suggestions what I should do??