Steam reboilers

Status
Not open for further replies.

sfacchin

Chemical
May 13, 2009
19
S!
I'm kind lost about the principles behind a thermosiphon steam reboiler. I'm mean: when it's necessaty to increase the heat duty, normally, in a steam flow/reboiler level cascade control strategy, the set point of the reboiler level is decreased. The resulting increase of heat duty is consequece of the an larger heat exchange surface, or is consequence of a bigger temperature difference between the steam's temperature (lower as consequence of the smaller pressure - steam expasion due to increase of "free" volume) and wall/boiling liquid's temperature, or is a sum of both effects?
New+Picture+%285%29.png
 
Replies continue below

Recommended for you

The most common method to vary the heat flux in a thermosyphon reboiler is to use a valve in the steam supply to the reboiler. Adjusting this valve varies the pressure in the steam chest and since the condensation pressure fixes the condensation temperature you are able to set the temperature driving force. In this case a steam trap would be used to discharge the condensate while maintaining the back pressure.

Another method, which is less common, is to put the control valve in the condensate outlet. This works by varying the back-up of condensate in the steam chest, thus effectively making the reboiler a variable-area device since the heat transfer coefficient from the liquid condensate is negligible compared with the HTC for the condensing steam.

Considering the classic heat transfer equation of
Q = U x A x [Δ]t
in the first scenario you are varying [Δ]t while in the second you are varying A. In both cases U is constant.

Katmar Software
Engineering & Risk Analysis Software
 
S!
Hum, I see.
Here we have a composition of the alternatives. The heat duty control loop uses a cascade control. The steam inlet (t/h) sets the set point of the level in the condensate drum. The level control manipulates the condensate's outlet valve.
What would be the main mechanism behind?
Thanks
 
What is the relative height of the condensate drum compared with the reboiler? If the level in the condensate drum is between the top and bottom of the reboiler tubes then it is functioning exactly like the second example I gave because the level in the reboiler would be virtually the same as in the drum.

If the condensate drum is below the reboiler then I cannot understand how it functions. If you could post a sketch it would help.

Katmar Software
Engineering & Risk Analysis Software
 
S!
The drum is leveled with reboilers.
Thank you.
Cheers.
 