Steel Beam bearing on stud wall 1
WARose
5,593
I have a situation where I'm going to have a steel beam come down and sit on a stud wall. Does anyone have a detail for this? A Simpson connection maybe? Pretty much all the connections I am envisioning are going to have issues as far as providing the proper rotational restraint AISC expects.
Why would you need rotational restraint?
In section F1 of AISC (13th Ed., p.16.1-46) it says: “The provisions in this chapter are based on the assumption that points of support for beams and girders are restrained against rotation about their longitudinal axis.”
I personally think you can satisfy that by torsional support at other locations (or just overall).....but it's got to be somewhere.
Provide an end plate or stiffeners at the beam bearing point and bolt the bottom flange to the wood. In the 13th edition manual, check out page 2-13 and 2-14.
Ian Riley, PE, SE
Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
Here's a detail I have used in the past:
Ian Riley, PE, SE
Yeah, I thought about using stiffeners myself....but the architect is insisting on some (wood) enclosure for the beam that precludes it. Thanks for the detail.
I've not put a steel beam on a wood stud wall... but, have used OWSJs bearing on stud walls... just created a bearing plate to transfer the load in compression perp to the grain and a couple of holes in the plate for attachment.
Dik
If you attach a wood nailer to the top of the beam to nail off the plywood diaphragm, and provide a connection to the column below, you have satosfied rotational restraint.
Mike McCann, PE, SE (WA)
If the beam is under a plywood diaphragm, why would the architect insist on a wood enclosure around the beam?
BA
If the beam is under a plywood diaphragm,....
It isn't.
.....why would the architect insist on a wood enclosure around the beam?
And thereby hangs a tale......it's a complicated situation.....but the beam will be visible in the room (due in part to it's depth). I tried to talk the architect into just a wood "box" around the perimeter.....but he is insisting on covering each face with wood to where it looks like a gigantic wood beam.
Creative guys aren't they? [smile]
Tell him you can use ironwood and make an I beam for him.
M^2... ever try working with that stuff... rather than cutting it to fit, it would likely be easier to weld... It is really tough stuff...
Dik
My son made a deck with it.
Yes, Tough and very expensive.
Have to predrilled all connections.
Will the architect allow a steel post in the stud wall? Something like a 3"pipe with a bearing plate on both ends.