Steel Beam Fire Proofing

Status
Not open for further replies.

ChrisAFP

Mechanical
Nov 10, 2011
2
Our company recently completed a fire sprinkler project in a existing nursing home. Some of the spray-on fire proofing was disturbed by attaching beam clamps to the structural steel.
The facility is fine with this, but the Engineer is looking for us to "touch-up" every where this situation occurred.
Has anyone ever encountered this before?
 
Replies continue below

Recommended for you

would be similar to penetrating a rated wall, needs to be properly protected.
 
I commonly require these corrections on spray applied fire resistive materials, especially in high-rise buildings.
 