mappryan
Structural
- Mar 11, 2011
- 8
Ok, to start out let me describe the situation here. My firm has been contracted to perform a failure investigation on an existing HSS 6x6x1/4 column. The building was constructed in 1994 as a grocery store. The building is currently in the process of being converted to a department store. During demolition of the building this HSS column buckled and sheared right through its compression flange (see attachment). The project manager for the GC is adamant that the column was struck at about 5' from the base by the trackhoe operator. Of course the trackhoe operator says that is absolutely not the case. I am an EI with little to no experience in this type of failure and would greatly appreciate any help or insight into the possible causes. Here is the pertinent information (hopefully I dont omit anything).
- HSS 6x6x1/4
- Unbraced Length is ~26 ft
- Tributary Area supported by column ~1430sq ft
- Typical Metal Deck roof
- Typical bar joist framing.
- Top is pinned. Base appears to be fixed(no baseplate visible)
- Failure point is about ~18ft from base
- significant rain occured earlier in the week (project manager noted water flowing from the scuppers and check and verified all (4) 10" dia. roof drains were working.
I determined in my analysis that the euler buckling load is ~74kips in a pin-pin configuration. Dividing this by the 1430 sq ft would mean a load of ~52 psf would be required to fail this column. I assumed 15psf for dead load and 20.8psf for 4" Rain Load but that still only brings me to 35psf. I am unsure how the impact at 5' from the base would cause the buckling at 18'. I understand that in the fixed-pin configuration the buckling would be shifted up from midpoint. Is is common for a column to shear right through itslef when it buckles? I have attached a few pictures and a portion of the plan where this occured. Any insight or opinions would be greatly appreciated. Thanks
- HSS 6x6x1/4
- Unbraced Length is ~26 ft
- Tributary Area supported by column ~1430sq ft
- Typical Metal Deck roof
- Typical bar joist framing.
- Top is pinned. Base appears to be fixed(no baseplate visible)
- Failure point is about ~18ft from base
- significant rain occured earlier in the week (project manager noted water flowing from the scuppers and check and verified all (4) 10" dia. roof drains were working.
I determined in my analysis that the euler buckling load is ~74kips in a pin-pin configuration. Dividing this by the 1430 sq ft would mean a load of ~52 psf would be required to fail this column. I assumed 15psf for dead load and 20.8psf for 4" Rain Load but that still only brings me to 35psf. I am unsure how the impact at 5' from the base would cause the buckling at 18'. I understand that in the fixed-pin configuration the buckling would be shifted up from midpoint. Is is common for a column to shear right through itslef when it buckles? I have attached a few pictures and a portion of the plan where this occured. Any insight or opinions would be greatly appreciated. Thanks