Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Steel Joist Bearing Depth 1

Status
Not open for further replies.

cfc

Structural
Dec 26, 1998
11
The typical bearing depth for a K-Series joist is 2 1/2". I have an alteration project where new joists will bear atop existing steel beams. I can add a new strucutral member atop the existing beams to achieve the standard 2 1/2" bearing depth. The other option is to specify a 3 5/8" bearing depth. Is this a viable option(i.e., do joist manufacturers allow this alternative)?

Thanks,
Charlie Canitz,PE
Bel Air, MD
 
Replies continue below

Recommended for you

Short span joists, those 24" or less in depth have a seat of 2.5" and long span joists, ie. greater than 24" deep typically have a seat depth of 5". This allows the diagonal web member to clear the bearing.
 
You can specify whatever joist seat you need for most SJI joist manufacturers. It does add to the cost a bit. Either way, there is additional cost as adding the steel to the top of the existing beam will include small material costs but field labor/welding.

Also, be aware that if your deck takes lateral shear forces and has to drag them into the beam below, the higher joist seat could be a problem (with lateral loads perpendicular to the joists, the seats will be loaded to roll over sideways). You can take care of this by adding steel between the beam and deck to take the lateral forces.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor