jochav52802
Structural
- Nov 28, 2018
- 81
Good Day!
Regarding steel joist bend loads, when we go to hang MEP components from our joists, it's common practice to support these items by spanning angles or channels between either the joist top or bottom chord.
As a result, our steel typically only attaches to one of the two chord angles, and a lot of the time there are no connectors between the angles outside the joist panel points, so concentrated loads applied outside panel points can't be load-shared between both angles.
My questions are as follows:
1) When a bend load is specified, does that assume that the load will be equally supported by both joist chord angles?
2) When I attach my MEP support steel to one of the joist chord angles, does that imply that the available bend load must be cut in half?
The standard detail I've seen for local joist reinforcement doesn't clarify this, so it seems that a lot of Engineers could be misled into thinking that they have double the bend-load capacity, and thereby missing areas where local reinforcement is required.
Any thoughts are appreciated, thank you!
Regarding steel joist bend loads, when we go to hang MEP components from our joists, it's common practice to support these items by spanning angles or channels between either the joist top or bottom chord.
As a result, our steel typically only attaches to one of the two chord angles, and a lot of the time there are no connectors between the angles outside the joist panel points, so concentrated loads applied outside panel points can't be load-shared between both angles.
My questions are as follows:
1) When a bend load is specified, does that assume that the load will be equally supported by both joist chord angles?
2) When I attach my MEP support steel to one of the joist chord angles, does that imply that the available bend load must be cut in half?
The standard detail I've seen for local joist reinforcement doesn't clarify this, so it seems that a lot of Engineers could be misled into thinking that they have double the bend-load capacity, and thereby missing areas where local reinforcement is required.
Any thoughts are appreciated, thank you!