Can one safetly use joist bottom chord extensions to provide adequate lateral bracing requirement for a beam column in a roof or a floor diaphragm? If so what is the magnitude of axial forces to provide the joist manufacturer?
Is there also any code provision that deal with this situation? Which one and where?
 
Replies continue below

Recommended for you

What is a beam column that supports a joist? The top chord of a joist can be used to brace the compression flange of a beam if the other end is attached to a wall or a stable member.
 
I see joist bottom chords used to stabilize joist girders at ~1/3 and the ~2/3 span region of the JG almost every time i see joist and joist girders together. i inspect steel and rarely design it however.
 