spats
Structural
- Aug 2, 2002
- 655
I am designing exterior steel stair guardrail where the infill panels are perforated metal, as specified by the architect. The attached file shows a typical infill panel. By code, the infill for a guardrail needs to resist 50 lbs. applied to a 1' square area. Being exterior, wind load should probably also enter the conversation. Calculations are required for the shop drawing submittal. Question is, how the heck do you calculate such a thing short of a finite element analysis? In some respect, the whole thing could go into some sort of catenary suspension. How would you handle this? It's not going anywhere if it "fails", and I'm not doing finite element analysis.