While I guess one could argue the relevance to stormwater or culvert applications, you may be interested in the information contained in The Ten States Standards document at
including,
“33.45 High Velocity Protection
Where velocities greater than 15 feet per second (4.6 m/s) are attained, special provision shall be made to protect against displacement by erosion and impact.
33.46 Steep Slope Protection
Sewers on 20 percent slopes or greater shall be anchored securely with concrete, or equal, anchors spaced as follows:
a. Not over 36 feet (11 m) center to center on grades 20 percent and up to 35 percent;
b. Not over 24 feet (7.3 m) center to center on grades 35 percent and up to 50 percent; and
c. Not over 16 feet (4.9 m) center to center on grades 50 percent and over.”
See also with regard to cvg’s guidance maybe away from RCP for such situations what appears to be (for whatever reasons) a concurring statement on page 372 of the reference at
.
I would also note ductile iron pipes are also sometimes used on steep slopes as they have rather good constructability and toughness e.g. to resist concentrated support reactions etc. (e.g. see
and
etc.), though on very steep slopes I would think restrained joint pipes at least would most often be specified, and particularly if there is less than one support/anchorage per stick of pipe. While certainly not professing to be any sort of expert in all aspects of very steep sewer/pipeline constructions, I would think if it is possible (and it would appear maybe it would in this case) to somehow key the “cut-off walls”, anchors/supports, or whatever one wants to call them into solid rock, that would perhaps also be helpful to keep “the whole shooting match” (pipeline and bedding) from sliding downhill, under the rather inexorable forces of gravity and water movement etc.