Stem Purge Pressure and Valve ASME Pressure Rating

Status
Not open for further replies.

McT178

Mechanical
Nov 17, 2010
48
I have a valve with a stream purged stuffing box that is designed and rated for 50 psi, and the maximum purge pressure is 100 psi. Is there a code exemption for the purge pressure being that the flow rate of the purge is insignificant to the flow rate of the valve - like a drop in the ocean with no chance of over pressuring the valve? Or, will the purge line need pressure controls limiting the pressure to MAWP of the valve?
 
Replies continue below

Recommended for you



If I understand you correct here, I believe the answer is quite simple. You can not, in my opinion, pressurize a cavity connected to a total pressurized system, with a source supplying a pressure higher than the allowed for the total system.

 