rockman7892
Electrical
- Apr 7, 2008
- 1,161
I'm reviewing an application in which 480V paralleling switchgear feeds a circuit which steps voltage up to 4.16kV for transmission over a long distance before it is stepped back down to 480V for use in the 480V emergency system.
The feeder breaker in the paralleling switchgear is a 3000A breaker which feeds a 2000kVA 480V - 4.16kV step up transformer with a 450A fused switch coupled on transformer secondary. From this transformer the cables travel some distance before hitting new substation which has a 750kVA 4.16k-480V step down transformer with a 150A primary switch and a 1600A 480V breaker in the downstream switchboard.
Are there any special consideration that need to be given to the protection & coordination of such a circuit aside from the considerations given to a normal MV single transformer step-down circuit?
What kind of inrush would the paralleling switchgear feeder see from the two transformers being energized in series? Would it still only see the inrush from the first initial step-up transformer and not really see the inrush of the downstream step-down transformer.
NEC Table 450.3(A) does not provide requirements for primary breaker protection with a breaker 600V or less (only for 600V or less with secondary protection). Are there requirement that govern the 480V feeder breaker on the LV side of the step-up transformer.
The feeder breaker in the paralleling switchgear is a 3000A breaker which feeds a 2000kVA 480V - 4.16kV step up transformer with a 450A fused switch coupled on transformer secondary. From this transformer the cables travel some distance before hitting new substation which has a 750kVA 4.16k-480V step down transformer with a 150A primary switch and a 1600A 480V breaker in the downstream switchboard.
Are there any special consideration that need to be given to the protection & coordination of such a circuit aside from the considerations given to a normal MV single transformer step-down circuit?
What kind of inrush would the paralleling switchgear feeder see from the two transformers being energized in series? Would it still only see the inrush from the first initial step-up transformer and not really see the inrush of the downstream step-down transformer.
NEC Table 450.3(A) does not provide requirements for primary breaker protection with a breaker 600V or less (only for 600V or less with secondary protection). Are there requirement that govern the 480V feeder breaker on the LV side of the step-up transformer.