We have a DC system that requires a battery to supply the following stepped load:
1. 129kW for 15 minutes, then,
2. 106kW for 15 minutes, then,
3. 100kW for 60 minutes, then,
4. 18.5kW for 90 minutes
I have contacted battery manufacturers and they disagree on the way the stepped load is simplified for battery autonomy.
Some say that the 129kW should be taken and then ratios used on the time which gives 129kW for 87 minutes.
Others say that the time is taken and then ratios used on the power which gives 62.17kW for 180 minutes.
A battery discharge curve is none linear and has different characteristics at the 87 minute rate compared to the 180 minute rate, e.g. Powersafe 2V275 1 hour wpc to 1.7V at 20 degrees is 329.4 and at the 3 hour rate is 136.8.
Which is the correct method?