How to evaluate the stiffness EI of a composite beam (like W24 encased inside a 36 in diameter 4000 psi concrete) considering the craking effect in concrete? Thank you very much.
 
Replies continue below

Recommended for you

Probably much like ACI does to develop their Ie value in Chapter 9.

I would look at the unfactored load stress condition and discount any concrete that was in a tension zone. You could include rebar in the tension and compression zones as well - just transform the concrete in compression to steel - with a circular cross section that is much more difficult - you'd end up with an ellipse when factoring the width down by n=Es/Ec.

You could perhaps take segments of the compresssion portion of the circular concrete section and transform each one down. Then just calculate your properties.

ACI treats a concrete section for determination of moment of inertia using a transition between the non-cracked and fully cracked conditions. This is their Ie formula where they discount some of the stiffness before the section reaches the cracking moment. I presume you could do something like that here...just not sure of the step-by-step process.

AISC has a nice section in their LRFD manual (second edition) on page 5-67 where they deal with composite columns - check that out and see if it helps you.
 