Good morning,
I have a 8' x 8' x 3' deep spread footing supporting a 4' circular concrete column supporting one end of a sign structure.
The dead load (~70 kips) is small compared to the moment (~550 kip-ft) and overturning is a concern. The geotech engineer provided 4 post-tensioned (~65 kips) ground anchors in each corner of the footing.
Not having done much in the way of footings or strut-and-tie, I had a few questions.
When I run the STM, is the column rebar coming down ok for use to resist the tension in the vertical ties?
Do I need shear reinforcement? The concrete has enough capacity to resist the punching shear forces but do I still need anything in the way of minimum shear reinforcement as a good practice? Given the dimensions, I didn't check one-way shear. Rebar congestion is an issue - I need top and bottom bars each way and bursting reinforcement around the ground anchors. There is also rebar coming in from the column hooking into the footing plus ties for the column rebar.
Do I need additional spalling reinforcement? There is main bar in both directions to pick up the relatively small spalling force but I'm not sure of that failure plane. I would not want the concrete to suffer large cracks before engaging the main bars.
Thank you in advance.
I have a 8' x 8' x 3' deep spread footing supporting a 4' circular concrete column supporting one end of a sign structure.
The dead load (~70 kips) is small compared to the moment (~550 kip-ft) and overturning is a concern. The geotech engineer provided 4 post-tensioned (~65 kips) ground anchors in each corner of the footing.
Not having done much in the way of footings or strut-and-tie, I had a few questions.
When I run the STM, is the column rebar coming down ok for use to resist the tension in the vertical ties?
Do I need shear reinforcement? The concrete has enough capacity to resist the punching shear forces but do I still need anything in the way of minimum shear reinforcement as a good practice? Given the dimensions, I didn't check one-way shear. Rebar congestion is an issue - I need top and bottom bars each way and bursting reinforcement around the ground anchors. There is also rebar coming in from the column hooking into the footing plus ties for the column rebar.
Do I need additional spalling reinforcement? There is main bar in both directions to pick up the relatively small spalling force but I'm not sure of that failure plane. I would not want the concrete to suffer large cracks before engaging the main bars.
Thank you in advance.