pipesnpumps
Mechanical
- Dec 4, 2002
- 316
There is something I don't understand with the IBC 2006, Table 508.3.3. This is kind of related to NFPA codes, so not out of line to post here..
An example:
A sprinklered building that is an IBC business occupancy (B) has a storage area that is >3,000 sq ft, and it is chosen to have the storage area "separated" per IBC definition with a fire barrier.
The storage to be separated has combustible materials, so therefore it is group "S-1" (moderate hazard, aka combustible) storage. Table 508.3.3 shows that S-1 to B fire barrier is No separation required.
But comma however, if the storage had been chose as S-2 (low hazard aka non-combustible) storage, it would require a 1 hour fire barrier for S-2 to B..
NFPA 101 would be 1 hour for separated occupancies.
What the heck, over?