during internal inspection of a floating roof storage tank, we have detected external corrosion of annular plat of the floor
this corrosion is localised in the 100 mm inward from the shell and sems to be a goove corrosion with the remaining thickness of 2 mm in some areas
the legs of the weld of the shell to bottom is free from corrosion and the thickness of the projection of the annular plat outside the shell is 4 mm
according to API 653 table 4.5 the min thickness of the annular plat for our case is 0.17 in (stress < 24300 psi and thickness of first shell course < 0.75 in)
my question is:
Before changing the annular plat, it is tolerable to put the tank in service with a maximum fill hight of 6 meter (insted of original maximum fill hight 17 meter) corresponding to a stress of 7597 psi of the first shell course
what is the type of failure if there is any risk to put the tank in service
the tank characteristics are as follow:
hight: 17.16 meter
diameter:35.2 meter
thikness of first shell cours: 17,8 mm
bottom thickness: 6 mm
annular plat thickness: 9.5 mm
storage volum: 16620000 Litres
storage fluid: stabilized oil
during internal inspection of a floating roof storage tank, we have detected external corrosion of annular plat of the floor
this corrosion is localised in the 100 mm inward from the shell and sems to be a goove corrosion with the remaining thickness of 2 mm in some areas
the legs of the weld of the shell to bottom is free from corrosion and the thickness of the projection of the annular plat outside the shell is 4 mm
according to API 653 table 4.5 the min thickness of the annular plat for our case is 0.17 in (stress < 24300 psi and thickness of first shell course < 0.75 in)
my question is:
Before changing the annular plat, it is tolerable to put the tank in service with a maximum fill hight of 6 meter (insted of original maximum fill hight 17 meter) corresponding to a stress of 7597 psi of the first shell course
what is the type of failure if there is any risk to put the tank in service
the tank characteristics are as follow:
hight: 17.16 meter
diameter:35.2 meter
thikness of first shell cours: 17,8 mm
bottom thickness: 6 mm
annular plat thickness: 9.5 mm
storage volum: 16620000 Litres
storage fluid: stabilized oil