wcl77
Structural
- Nov 13, 2006
- 5
I need a bit of guidance in tackling my most recent work assignment. I have a RC rectangular box storage tank (60-ft long and 20-ft wide and 13-ft deep) that contains sulfur. The storage tank is located in a refinery. I need to punch a hole (18-inches x 30-inches) in the top slab (13-inches thick with No. 6 @ 8" e.f. e.w.) to permit the installation of a submersible pump. There is no additional load on the top slab as top of slab is 6-inches above grade.
I am interested in methods of analysis (ACI 318?) to determine if the existing slab will support the load from the new pump (approx. 4.5 kips dead weight and 2.5 kips operating weight) and possible retrofits to the slab in the area of the new opening to ensure a safe and reliable design (already plan on sealing cut concrete with chemical resistant epoxy paint). My gut tells me there is plenty of flexural and shear capacity in the two way slab.
Any other pointers will also be appreciated.
I am interested in methods of analysis (ACI 318?) to determine if the existing slab will support the load from the new pump (approx. 4.5 kips dead weight and 2.5 kips operating weight) and possible retrofits to the slab in the area of the new opening to ensure a safe and reliable design (already plan on sealing cut concrete with chemical resistant epoxy paint). My gut tells me there is plenty of flexural and shear capacity in the two way slab.
Any other pointers will also be appreciated.