Hi everybody. Looking for thoughts/comments/guides.
base on API 2000 storage tanks are
"... tanks designed for operation at pressures from full vacuum through 103.4 kPa (ga) (15 psig)."
and based on api 14c:
atmospheric service has
"Operation at gauge pressures between 0.5 ounce psi (0.2 kPa) vacuum and 5 psi (35 kPa) pressure."
why definition/criteria for atmospheric tanks for two API standards are totally different?
my next question is about PVRV. API 14c says:
"A second vent may be installed in lieu of the PVRV." In the other hand we can delete PVRV and instead of PVRV use another vent line! are we allowed do this.
I appreciate for any respond.