Is my understanding correct? ->

For most large curtain wall systems there are T and F anchors which fit inside the vertical mullion. These anchor the system to the substrate and allow for vertical movement of the substrate and thermal/expansion contraction of the mullion. However for most single story storefront systems, these anchors are not used. Typically the vertical mullion is fastened to the head and sill mullion (via a shear block) and the head and sill mullions are fastened to the substrate. However, a gap is present between the storefront and the substrate (say 3/8 - 1/2 or whatever is needed). In order to achieve this gap, the anchor is checked in bending. Typically a fixed-guided end conditions are assumed. I could see anchoring into steel, concrete or wood as being fixed, but what about cold formed steel? I could see the aluminum mullion, if it were a tube section as providing as a guided condition, but what about when it is a channel, or you are fastening through the thermal break material? Find attached for further explanation.

Also I typically see extra fasteners at jambs, maybe for wind load or door weight? I don't normally see calcs for door weight or operable windows but it's possible I just haven't seen enough examples.

EIT
www.HowToEngineer.com
 
 http://files.engineering.com/getfile.aspx?folder=fe20fcf9-9f7e-464a-8cb8-6bb1561338b4&file=Storefront_anchorage.pdf
Replies continue below

Recommended for you

As a light gage steel designer, I don't know how they get this stuff to work. It probably does not work out on paper but they seem to perform OK in reality.
 
Thanks for the response.
We also do a fair amount of CFS and I know what you mean. I have been going over some example projects from other companies and it seems like what I am describing is what they are assuming. However most projects are for larger curtain walls with the T&F anchors and all works out a little easier. With a storefront or window, it seems that the anchor is the cantilever member. I'm not sure how this works with CFS though. I suppose you could still resolve the moment caused by the eccentricity with a tension in the anchor and compression on the edge of the mullion.

EIT
 
Please excuse my ignorance, but what are "T & F" anchors?
 
Thank you Ingenuity, I was hoping somebody would ask that question or it would become clear from context.

Jim.
 
They are connections used to anchor vertical mullions to a horizontal surface (e.g. slab). They are typically used with 2 post-installed anchors. The 'T" has one anchor on each side of the mullion. The "F" has 2 anchors on one side of the mullion. The "F" are used in places such as door openings.
 
Yes, as explained by WannabeSE. The 'stem' of the "T" fits into the vertical mullion so that the Vertical mullion can slide up/down. The stem does not actually fasten to the Vertical Mullion.

So I'm guessing that there really is no standard way for the storefront situation...

EIT
 
Thanks wannabeSE and RFreund.

Found this, jimstructures, that helped me 'picture' what they are exactly:

T_f_ANCHORS_vbs1n5.png
 
...and there are J anchors too...maybe other letters of the alphabet are represented too ;-)

j_hdjh3y.png
 