Section 303.3 of the ICC500 states: "Underground portions of storm shelters shall be designed for buoyancy forces and hydrostatic loads assuming that the ground water level is at the surface of the ground at the entrance to the storm shelter, unless adequate drainage is available to justify designing for a lower ground water level."
My interpretation of this is that if you are designing an underground storm shelter, you must assume the ground water level is at grade and subsequently you must design for the hydrostatic and buoyancy loads that come with this.
We are currently designing a storm shelter that is above-ground with shallow foundations. I am having a disagreement with my coworker who is saying that you must also design the foundations assuming ground water level is at finished grade (which is +/- 3' below finish floor). Is this interpretation of the code correct? I am getting insanely large footing sizes since the buoyancy force uplift is equivalent to the volume of the foundations displaced by water.