twangmaster
Mechanical
- Aug 28, 2003
- 1
We've got an office, approx. 2400 sq. ft. w/ open structure ceiling at 14'. We're putting 3200 cfm w/ 200/250 mbh gas heat rooftop unit. The unit is tripping out on high limits, finally found out we were getting 88F return temp. When the unit is shut down, and the fan off, we waited about 30 min. started unit back up. return temp was 74F. Duct system is exposed with spiral duct, with diffusers angled at 45 degress toward the exterior walls from a 10' elevation. Return is at approximately 12'. Since i'm seeing a 74F return temp when the unit is first starting up, i'm thinking that it's not stratification, but rather short-circuiting from the supply diffusers to the return. Any ideas? Thanks!