Wasn't sure whether to post this question here or in the electrical area, so I will probably post a link to this question from there.
We have a legacy installation of large crude oil storage tanks which are equipped with motor-driven mixers located low in the wall of the tank designed to keep the oil in gentle motion. Each tank is protected by a dedicated ICCP system with groundbeds local to the tank bund. In addition to the mixers, the tanks have the typical level instrumentation and electrically-actuated valves.
The motors are fed from a remote substation and the cable is a steel wire armoured type which is connected to the substation's earthing array. The cable armour provides a path for current to return to the source in the event of a fault. The motors are located in an ATEX Zone 2 which is loosely equivalent to a North American Div 2. There are fairly prescriptive rules about what can and can't be done with electrical equipment in this type of location.
The armour of the mixers provides a path for current from the ICCP system to enter the earth at the substation's copper earthing grid, bleeding current off the rectifiers and resulting in much higher groundbed currents to achieve adequate potential shift on the tank. It also provides a route for the ICCP systems on neighbouring tanks to interact. The mixers are particularly problematic because the cables are large and the cable armour resistance is low, so although there are some currents flowing the armour of the valve actuator and instrument cables the currents are much smaller than those in the mixer cables.
I'm interested in what other users have implemented in this scenario to meet the conflicting requirements of the ICCP system which would tend to introduce isolation flanges and joints to control stray currents, and the electrical and ATEX rules which at a simplistic level would tend to bond everything together. I'm not especially happy about heavy DC currents flowing in cable armour where disconnecting the cable could result in an incendive spark, but I'm not seeing any acceptable alternatives either. I'm inheriting this mess, so if someone has solved the problem before I'd appreciate some hints where to look.
We have a legacy installation of large crude oil storage tanks which are equipped with motor-driven mixers located low in the wall of the tank designed to keep the oil in gentle motion. Each tank is protected by a dedicated ICCP system with groundbeds local to the tank bund. In addition to the mixers, the tanks have the typical level instrumentation and electrically-actuated valves.
The motors are fed from a remote substation and the cable is a steel wire armoured type which is connected to the substation's earthing array. The cable armour provides a path for current to return to the source in the event of a fault. The motors are located in an ATEX Zone 2 which is loosely equivalent to a North American Div 2. There are fairly prescriptive rules about what can and can't be done with electrical equipment in this type of location.
The armour of the mixers provides a path for current from the ICCP system to enter the earth at the substation's copper earthing grid, bleeding current off the rectifiers and resulting in much higher groundbed currents to achieve adequate potential shift on the tank. It also provides a route for the ICCP systems on neighbouring tanks to interact. The mixers are particularly problematic because the cables are large and the cable armour resistance is low, so although there are some currents flowing the armour of the valve actuator and instrument cables the currents are much smaller than those in the mixer cables.
I'm interested in what other users have implemented in this scenario to meet the conflicting requirements of the ICCP system which would tend to introduce isolation flanges and joints to control stray currents, and the electrical and ATEX rules which at a simplistic level would tend to bond everything together. I'm not especially happy about heavy DC currents flowing in cable armour where disconnecting the cable could result in an incendive spark, but I'm not seeing any acceptable alternatives either. I'm inheriting this mess, so if someone has solved the problem before I'd appreciate some hints where to look.