First here is some back ground. 3-phase 4160v system. Each phase feeds 4 2400/120-240 transformers.
The original system had a direct burried conductor with a bare concentric neutral (no jacket). It was a 25 year old system.
The system was upgraded with new 1/0 Al tape shielded cable in conduit. (no concentric neutral). This is per an engineers drawing. There is a #6 copper that was pulled for a ground, but is now acting as the neutral.
The #6 is landed on the H0 of the transformer, which is part of the transformer enclosure. The enclosure is grounded with a ground rod, and there is a bond jumper from the enclosure to the XO. There are multiple secondarys running out to trailer pedistals, which also have a bond jumper from neutral to ground.
This is a master meter trailer park.
After the cable was replaced the park started having strange stray voltage problems. People getting zapped from there trailers, Cable/tv lines burning into. Arcing from cable tv to trailer skins. There was a measured voltage of up to 30volts from the metal of the trailer to the dirt.
At each transformer two more ground rods were diven. One connected to the can on the primary side and the other to the can on the secondary side.
Most of the stray voltage is now under control. But there is still 4volts showing from the ground to the neutral. This voltage still shows up on a pedistal with the jumper removed, and the transformer feeding that section turned off. Primary still live running to pot switch in transformer and out to next one in line.
The bond jumper in the transformers is showing 40 to 60 amps.
I hope this is enough info to help, Ive been scratching my head big time. I think the cause is the #6 neutral causing a high impedance path back to the SES. This causing the voltage to seek lowest imedance path forcing it to ground/ or cable tv system which is grounded to the hilt.
If anyone has any idea to try ? Let me know
The original system had a direct burried conductor with a bare concentric neutral (no jacket). It was a 25 year old system.
The system was upgraded with new 1/0 Al tape shielded cable in conduit. (no concentric neutral). This is per an engineers drawing. There is a #6 copper that was pulled for a ground, but is now acting as the neutral.
The #6 is landed on the H0 of the transformer, which is part of the transformer enclosure. The enclosure is grounded with a ground rod, and there is a bond jumper from the enclosure to the XO. There are multiple secondarys running out to trailer pedistals, which also have a bond jumper from neutral to ground.
This is a master meter trailer park.
After the cable was replaced the park started having strange stray voltage problems. People getting zapped from there trailers, Cable/tv lines burning into. Arcing from cable tv to trailer skins. There was a measured voltage of up to 30volts from the metal of the trailer to the dirt.
At each transformer two more ground rods were diven. One connected to the can on the primary side and the other to the can on the secondary side.
Most of the stray voltage is now under control. But there is still 4volts showing from the ground to the neutral. This voltage still shows up on a pedistal with the jumper removed, and the transformer feeding that section turned off. Primary still live running to pot switch in transformer and out to next one in line.
The bond jumper in the transformers is showing 40 to 60 amps.
I hope this is enough info to help, Ive been scratching my head big time. I think the cause is the #6 neutral causing a high impedance path back to the SES. This causing the voltage to seek lowest imedance path forcing it to ground/ or cable tv system which is grounded to the hilt.
If anyone has any idea to try ? Let me know