structural design of brick arch 1
PSUengineer1
145
thank you for reading.
Looking at 1800s brick arch opening. span is 7 feet. rise is 3.5 feet. vertical cracks at top of opening. vertical offset between brick at top of opening around 1/4 inch.
is there a design standard someone can refer me to in order to check this? This is on a small wall (about 10 feet long) on a side porch. Half the wall was falling down, has been reconstructed, and is now cracking again. trying to figure out why, maybe the span/rise ratio?
Please let me know if you have design info i can check against on historical arches. Or if you know of why this is happening please share your experience.
thanks.
The below link gives good design guidance which I’ve used in the past. If its an old arch though there are many variables - foundation settlement, mortar decaying, brick decaying, thermal movements etc.
Is the crack uniform width? Wider at the top or bottom?
Is there enough wall on either side of the arch to provide the necessary lateral restraint?
I’m guessing not. It’s a very common failure, a masonry arch with insufficient abutment starts doing the splits...
"Is there enough wall on either side of the arch to provide the necessary lateral restraint?"
Also my first thought. 7 foot span, 10 foot long wall. Better be tied into something stronger that an 18" brick wall pier.
I agree with Celt83 about checking with Professor Boothby. He wrote a paper called "A Visual Classification System for Masonry Arch Failures" that shows some of the common failures of masonry arches. You can see the paper here: but you still may want to contact Prof. Boothby since he has developed other tools to analyze arches. In most cases its all about the abutments and their movement.
thanks to all who replied. The Boothby paper is definitely worth a read.