I am designing connection for two wood beams connected to each other by bolts or lag screws. The lag screw or bolts are provided in three rows and at a certain spacing along the length of beams. How the check for the connection strength if a udl is acting on the combined beam along the length.

Thanks.
 
Replies continue below

Recommended for you

You should consider uploading a sketch of your condition, to get the most helpful responses.

If the UDL is acting evenly on the combined beam (and the connected beams are of the same section), then there is no structural need for the connection unless perhaps to provide additional stability for slender beams.

If the beams are of different sections, or if the UDL is applied directly to one beam and not the other, then there are calculations that can be performed.
 
In addition, you might try 2 lines of bolts staggered to reduce the number by more than half. The fasteners serve little purpose.

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
I agree with Dik. The connections will hold the beams together, but seem to add nothing in the way of strength. The beams should be treated as (2) separate beams.