We have an existing building which is changing occupancies and we have to verify if the slab can handle assembly load.
We're trying to make this detail work for strut and tie, something we haven't spent much time on, and wondered if there was a requirement for horizontal ties. In ACI 318-11 11.8.4 requires ties and its explained in 11.8.3.5 commentary. However in Appendix A there is no explicit requirement for these bars. The reinforcing shown in the attached sections easily handles the tension in the top tie (AB in most corbel truss models). The thickened slab shown in the section is a spandrel beam that runs parallel to the slab edge. At alternating columns we have the plan detail shown. This only impacts 1 column for this analysis.
Any insight would be helpful. Don't get me started on how awful an original detail this is.
RC
We have an existing building which is changing occupancies and we have to verify if the slab can handle assembly load.
We're trying to make this detail work for strut and tie, something we haven't spent much time on, and wondered if there was a requirement for horizontal ties. In ACI 318-11 11.8.4 requires ties and its explained in 11.8.3.5 commentary. However in Appendix A there is no explicit requirement for these bars. The reinforcing shown in the attached sections easily handles the tension in the top tie (AB in most corbel truss models). The thickened slab shown in the section is a spandrel beam that runs parallel to the slab edge. At alternating columns we have the plan detail shown. This only impacts 1 column for this analysis.