Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Subpanel question

Status
Not open for further replies.

RavenJoe

Electrical
Nov 26, 2001
17
I have a 100 amp 30 pole 3 phase 4w main 208/120 lighting panel. Fed by a 30 KVA transformer. This is an industrial application. Can I install a 3 phase 100 amp subpanel or should I go with a 60 amp ? What is the code on this and what is the article in the NEC?
 
Replies continue below

Recommended for you


The 100A breaker size described complies with 99 NEC Table 450-3(b).
 
You can install either one. The 60-amp subfed panel would require a 60-amp breaker in the 100-amp panel to feed it. The 100-amp sub-fed panel could be fed using feed-through lugs, no additional breaker required (lug out of the 100amp panel, main lugs only on the subfed panel).

Some jurisdictions (including Chicago) require a main breaker at all panels and/or don't permit subfeed lugs, beware of that.

Busbar's reference to 450-3 means that the max breaker for the transformer secondary is 200 amps, anything less than that is OK for the transformer.

But your panels are only rated for 100 amps, so the maximum breaker you can use is 100 amps to protect the panel bus. You can certainly use a single 100-amp breaker to protect two panels in series (unless the local AHJ has an issue as previously mentioned), they are both 100-amp panels and the breaker will limit the current they see to a maximum of 100 amps. I suppose the appropriate Code reference for that would be 240.4, which requires that conductors be protected against overcurrent.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor